I have 6 hot water tanks on site providing hot water in the washrooms. One of the tanks in EYFS is easily reached (the others are in roof voids).
Lately i have noted that the cylinder tank temp is only getting to 52 degrees before the tmv. The tmv is only a matter of 6 inches away from the tank. At first I thought it was because some clown had turned it of at the mains but no. I have turned the element up as far as it will go and put the timer onto continuous thinking it has not been on long enough. The element is not that old either. Has anyone any ideas what may be the problem.
Thanks.
Legionella temps.
Moderators: inspector, Dragonrider, jay, thecaretaker
- Maverick
- Registered Member
- Posts: 589
- Joined: 26th Dec 2018 at 10:02am
- Sparky
- Registered Member
- Posts: 703
- Joined: 12th Feb 2019 at 10:49pm
Dec 2022
13
20:02
Re: Legionella temps.
Has this been a slow or rapid drop in temperature? As in, what was your reading this time last month.
As you have said this is in a roof void, how well insulated is the tank and subsequent piping ? I’m no expert but could it be due to location and lack of insulation and with the drop in temperatures having an impact?
The other option ( depending on system type) is have a look for a tank stat. This is generally located 1/4 of they way up, held on by a strap. This could have come loose or faulty.
As you have said this is in a roof void, how well insulated is the tank and subsequent piping ? I’m no expert but could it be due to location and lack of insulation and with the drop in temperatures having an impact?
The other option ( depending on system type) is have a look for a tank stat. This is generally located 1/4 of they way up, held on by a strap. This could have come loose or faulty.